My current set up is a 240 volt line with 2 30 amp fuses. I guess that means the circuit is 60 amps. My new Olympic calls for a 45 amp. fuse. My question is can I safely run the new kiln on the 60 amp or do I need to install a 45amp fuse? Thanks in advance for any help.

Brad Walker
Site Admin
Posts: 1362
Joined: Fri Mar 07, 2003 9:33 pm
Location: North Carolina, USA
Contact:

Re: Kiln electrical question

Postby Brad Walker » Thu Oct 01, 2020 3:49 pm

You want it on the 60 amp. Don't install a 45 amp fuse, the fuse needs to be at least 10% (15% to 20% is better) higher than the what the kiln draws. So if a kiln draws 45 amps, a breaker of 60 amp is what you want.

Doug Zawodny
Posts: 6
Joined: Wed Feb 28, 2007 8:30 pm
Location: Sacramento California
Contact:

Re: Kiln electrical question

Postby Doug Zawodny » Thu Oct 01, 2020 8:47 pm

thank you!

The Hobbyist
Posts: 303
Joined: Sun Mar 09, 2003 7:09 pm
Location: Sun City West (NW Phoenix), AZ
Contact:

Re: Kiln electrical question

Postby The Hobbyist » Fri Oct 02, 2020 9:36 am

I thought the fuse was to protect the wiring not the appliance.

However, if the original setup was correct with a 60 amp fuse on a 4 awg wire then downgrading to a 45 amp fuse would be OK. But the reverse would be dangerous; replacing a 45 amp fuse on 6 awg wire with a 60 amp fuse.

I suppose you could put a second (45 amp) fuse at the kiln that is on a 60 amp/4 awg line.

Jim "The Hobbyist"
"With or without religion, good people can behave well and bad people can do evil; but for good people to do evil—that takes religion. " Steven Weinberg

Dick
Posts: 80
Joined: Sun May 01, 2005 9:34 pm
Location: San Diego
Contact:

Re: Kiln electrical question

Postby Dick » Fri Oct 02, 2020 2:03 pm

2 30 amp fuses DOES NOT equal 60 amps. It equals 30. For a 60 amp circuit you need either 2 60 amp fuses or a double pole 60 amp breaker. The wire would be #6 gauge copper. Anything less and you risk a fire if you require 60 amps