Kiln electrical question

Posted: Thu Oct 01, 2020 3:45 pm
by Doug Zawodny
My current set up is a 240 volt line with 2 30 amp fuses. I guess that means the circuit is 60 amps. My new Olympic calls for a 45 amp. fuse. My question is can I safely run the new kiln on the 60 amp or do I need to install a 45amp fuse? Thanks in advance for any help.

Re: Kiln electrical question

Posted: Thu Oct 01, 2020 3:49 pm
by Brad Walker
You want it on the 60 amp. Don't install a 45 amp fuse, the fuse needs to be at least 10% (15% to 20% is better) higher than the what the kiln draws. So if a kiln draws 45 amps, a breaker of 60 amp is what you want.

Re: Kiln electrical question

Posted: Thu Oct 01, 2020 8:47 pm
by Doug Zawodny
thank you!

Re: Kiln electrical question

Posted: Fri Oct 02, 2020 9:36 am
by The Hobbyist
I thought the fuse was to protect the wiring not the appliance.

However, if the original setup was correct with a 60 amp fuse on a 4 awg wire then downgrading to a 45 amp fuse would be OK. But the reverse would be dangerous; replacing a 45 amp fuse on 6 awg wire with a 60 amp fuse.

I suppose you could put a second (45 amp) fuse at the kiln that is on a 60 amp/4 awg line.

Jim "The Hobbyist"

Re: Kiln electrical question

Posted: Fri Oct 02, 2020 2:03 pm
by Dick
2 30 amp fuses DOES NOT equal 60 amps. It equals 30. For a 60 amp circuit you need either 2 60 amp fuses or a double pole 60 amp breaker. The wire would be #6 gauge copper. Anything less and you risk a fire if you require 60 amps