Post by Terry Gallentine »

I have two kilns which I seldom use at the same time. I would like to build ssr boxes on the wall by each kiln and then use a portable controller made with an RTC-1000 (containing low voltage receptacles and plugs for signal voltage, thermocouple and a separate power source). Does anyone have any experience with this type of thing?
Brad Walker
Site Admin
Posts: 1489
Joined: Fri Mar 07, 2003 9:33 pm
Location: North Carolina, USA
Contact:

Re: kiln controller question

Post by Brad Walker »

You should be able to set up a standalone controller into which you can plug whichever kiln you're using. Probably work best with a switchable two-in-one plug.
Terry Gallentine
Posts: 190
Joined: Mon Jul 19, 2004 2:08 pm
Location: River Falls, WI
Contact:

Re: kiln controller question

Post by Terry Gallentine »

Thanks Brad. Do you have any idea of how long a thermocouple lead can be before you lose accuracy on the temperature?
Brad Walker
Site Admin
Posts: 1489
Joined: Fri Mar 07, 2003 9:33 pm
Location: North Carolina, USA
Contact:

Re: kiln controller question

Post by Brad Walker »

Terry Gallentine wrote:Thanks Brad. Do you have any idea of how long a thermocouple lead can be before you lose accuracy on the temperature?
That's more of a question for someone like Tony Smith, but I did find this:
The length of a thermocouple has no effect on its measurement accuracy or its ability to transfer the signal to the instrument.
For more, check out this link:

http://rdccontrol.com/thermocouples/the ... le-wiring/
Terry Gallentine
Posts: 190
Joined: Mon Jul 19, 2004 2:08 pm
Location: River Falls, WI
Contact:

Re: kiln controller question

Post by Terry Gallentine »

Thanks again Brad. I was more concerned about the length of the wire leading to the thermocouple than the actual length of the thermocouple. The article that you sent me seems to suggest that the length of the wire shouldn't be much of a problem if it is less than 150' or so. I am thinking about centrally locating the controller and running low voltage wire to the thermocouples and to the ssr's.
Brad Walker
Site Admin
Posts: 1489
Joined: Fri Mar 07, 2003 9:33 pm
Location: North Carolina, USA
Contact:

Re: kiln controller question

Post by Brad Walker »

That's above my pay grade. I'm familiar with situations where you simply plug the kiln into the standalone controller and just plug in a different kiln as needed (as well as move the thermocouple), but don't have any experience with what you're wanting to do instead, other than to think it's a lot more complicated.
Kevin Midgley
Posts: 773
Joined: Mon Mar 10, 2003 11:36 am
Location: Tofino, British Columbia, Canada

Re: kiln controller question

Post by Kevin Midgley »

Digitry have as part of their system, little sending unit boxes which are fed by the thermocouple and then can be sent via 3 conductor 14/2 house type wire to the controller. No need to be close to the kiln with the digitry controller. The sending units also have a feature where they will buzz loudly should there be a thermocouple failure and alerting you to the problem and the controller is protected by Tiny Fuses. Sending unit wires from it to the controller must not be located beside regular building current wiring so as to avoid signal loss.
Without the sending units I might be worried about voltage drop from the thermocouple signal to the controller.
Terry Gallentine
Posts: 190
Joined: Mon Jul 19, 2004 2:08 pm
Location: River Falls, WI
Contact:

Re: kiln controller question

Post by Terry Gallentine »

Thanks everyone. I think that it is time to do some simple testing to see if the longer wires to the thermocouple maintain the same temp readings as the shorter wires.
Baxsie
Posts: 4
Joined: Fri Apr 12, 2019 2:23 pm

Re: kiln controller question

Post by Baxsie »

The important thing about thermocouple leads is that you do not splice them.

Thermocouple wire has one wire made of one kind of metal and the other made of a different metal. (ref https://en.wikipedia.org/wiki/Thermocouple )

A thermocouple measures the temperature by the change in voltage generated by the junction of two metals where they are welded together (the Seebeck effect, if you are keeping score).

If you splice the thermocouple with, for instance, copper speaker wire, you essentially make two more thermocouples with your two splices.

The same thing goes for connectors. You need to have special connectors where the parts are made of the same metals as the thermocouple's conductors. For example, if you have a Type K thermocouple, this connector might work:
https://www.amazon.com/Uxcell-a14032200 ... B00MJSLLCW

Also, note that the connector's two terminals are not the same. Each needs to be connected only to its corresponding wire of the same type of metal in the thermocouple wire.

It looks like kilns use either Type K or Type S thermocouples (ref: http://www.bigceramicstore.com/info/cer ... uples.html ) you would want to verify your thermocouple type, then purchase matching connectors.
Terry Gallentine
Posts: 190
Joined: Mon Jul 19, 2004 2:08 pm
Location: River Falls, WI
Contact:

Re: kiln controller question

Post by Terry Gallentine »

I have already gotten the type K connectors and type K extension wire. I am going to have a single length from the thermocouple to the controller. I am going to run some tests on a 25' run to make sure that the thermocouple is reading the same as with a much smaller run (5').
Kevin Midgley
Posts: 773
Joined: Mon Mar 10, 2003 11:36 am
Location: Tofino, British Columbia, Canada

Re: kiln controller question

Post by Kevin Midgley »

I was also told 40+ years ago that you were supposed to scrape the connector wire ends before making the connection with thermocouple leads.
And as well to tighten the connections and to re-tighten them an hour or so later.
The sending units with Digitry are nice.
Terry Gallentine
Posts: 190
Joined: Mon Jul 19, 2004 2:08 pm
Location: River Falls, WI
Contact:

Re: kiln controller question

Post by Terry Gallentine »

Thanks Kevin. That is good information that I will use when I set up my thermocouples.
Bert Weiss
Posts: 2339
Joined: Tue Mar 11, 2003 12:06 am
Location: Chatham NH
Contact:

Re: kiln controller question

Post by Bert Weiss »

I’ve done pretty long runs of thermocouple wire with no issues.

The idea of one outlet wired to the controller and plug either one in to run it is the simplest approach I know of. This can be hard wired with some sort of knife switch or something so you can divert the power to one side or the other.
Bert

Bert Weiss Art Glass*
http://www.customartglass.com
Furniture Lighting Sculpture Tableware
Architectural Commissions
Terry Gallentine
Posts: 190
Joined: Mon Jul 19, 2004 2:08 pm
Location: River Falls, WI
Contact:

Re: kiln controller question

Post by Terry Gallentine »

Thanks Bert,
I think that I am going to wire a single female to the controller and switch out thermocouple lines when I need to. I am going to use a low voltage toggles to switch signal voltage lines but I would be worried about doing the same thing with the thermocouple lines where current accuracy is extremely important.
Bert Weiss
Posts: 2339
Joined: Tue Mar 11, 2003 12:06 am
Location: Chatham NH
Contact:

Re: kiln controller question

Post by Bert Weiss »

Terry Gallentine wrote:Thanks Bert,
I think that I am going to wire a single female to the controller and switch out thermocouple lines when I need to. I am going to use a low voltage toggles to switch signal voltage lines but I would be worried about doing the same thing with the thermocouple lines where current accuracy is extremely important.
Thinking about this, you should be able to set up a box with 2 sets of wires coming in, and switch back and forth between sets. I would ask Krumor about it. They sell thermocouples, wire, and hardware. Their custom made thermocouples are top notch and not expensive. https://krumor.com/
Bert

Bert Weiss Art Glass*
http://www.customartglass.com
Furniture Lighting Sculpture Tableware
Architectural Commissions
Terry Gallentine
Posts: 190
Joined: Mon Jul 19, 2004 2:08 pm
Location: River Falls, WI
Contact:

Re: kiln controller question

Post by Terry Gallentine »

Thanks again Bert.